9/2/2010 12:38 PM | |
Posts: 2930 Rating:
|
Hi, A EM231 uses the 5v renge to meassure 0...20mA using the internel 250Ohm resistor. Now you use a 240Ohm resistor. Now you get: U = I*R U = 20mA * 240 Ohm U = 4,8V instead of 5V 5V = 32.000 (5V range used) 4,8V = 30720 (4,8V at 20mA) So you have to scale the standard AI from 0 .... 32.000 to 0 ... 30720. Best is to use the scal library. Link: http://support.automation.siemens.com/WW/view/en/27043396 1. Step scaleI to R 2. Step scale R to I Please checkit first. Hope this helps |
9/7/2010 3:39 AM | |
Posts: 2 Rating:
|
Thanks Helmut for the help! |