Hello forum users, Sinamics G120 with CU240S-DP-F or CU240E-2-DP. Can the digital outputs of the G120 be controlled by the PLC (via Profibus) ? Thanks in advance. |
6/14/2011 9:53 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, yes you can. set the telegram to 999 and connect the DO's via BICO to the telegramparameters. regards Christoph |