Hi KaRthickatr, Take a look here for GSD files. Kind regards, BV |
| 4/9/2012 12:58 PM | |
|
Joined: 10/7/2005 Last visit: 1/21/2026 Posts: 3054 Rating:
|
Hello KaRthickatr here's my take on things: 1.) Profibus GSD file for the Profibus DP Master module of the IM151-8 PN/DP CPU: Not available (and not needed, only Profibus DP Slaves have GSD files) 2.) ProfiNet GSD(ML) file for theIM151-8 PN/DP CPUitself: Not available "off the shelf", you create this one yourself from Step 7's HWconfig after you configured the IM151-8 PN/DP CPU as a so called "I-Slave". Have a look at chapter 4.8 of the SIMATIC PROFINET System Description manual which has all the details on how to do so. I hope this helps |
|