Hello S7Mgr the distinction between Peripheral (e.g. PIW, PQW) and Process Image related acccess (e.g. IW and QW) is only made inside theS7 program, which meansyour Atlas Copco DP Slave does not know nor cares about this (it's all I/O's for it, irrespective if the S7 treats them as Process Image and/or peripheral I/O's). As such, I can't really tell you what your problem is, but wonder if you S7 program perhaps usesProcess Image I/O'sbut does not have a large enough Process Image? Below are a couple of links whith more on this and I hope this helps: Where and when do you need peripheral addressing? Increasing PIP & PIQ vs. peripheral addressing |