2/3/2014 7:21 PM | |
Posts: 17 Rating:
|
Hellohdhosseini Thank you for your advise. In fact I'm using FB41 Cont_C, block (sorry, it was a type mistake in the Topic subject writing FC, instead of FB). Till now I've downloaded to the PLC CPU the CFC witch contains the PID control block FB41, but didn't reset yet the PLC, because at that moment can't shutdown the production line. In this PLC (S7-412-2DP),I've old software application built in FBD. Now I have the CFC tool integrated in Simatic Manager, and the new software applications are built using CFC. In the old applications using FBD I usually put in OB100 a set bit instruction, to set to 1 the COM_RST FB41 CONT_C bit. When the PLC restarts this instruction do a temporary (because is in the OB100) set to 1 of that bit, and the same to the others corresponding to other PID's I have in the application. In the CFC, when I have a PID block like the PB41 Cont_C, I don't see were this kind of instruction is done, but I see in the Proprieties of that block, the checkmark in the "To be inserted in OB/tasks: COMPLETE RESTART (complete restart)", thais the OB100. |
2/3/2014 9:49 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, In CFC it is poossible to monitor the I/O of blocks.It is also possible to modify the variable that are not assigned to any parameters in any chats.This should be done with care. Best regards, Hamid Hosseini |