Hello! Is there a driver GOT1000 for tia portal v13. I would like to do scada for GOT1000 GT14 using the Tia Portal v13. There is a possibility at all? |
3/7/2017 2:38 PM | |
Joined: 9/27/2006 Last visit: 9/1/2025 Posts: 12396 Rating:
|
Hello; As you gain experience with automation you will find out that when an HMI panel is developed by a different manufacturer than the PLC, it is up to the HMI manufacturer to provide connection information. In your case, you need to have a look at the information provided by Mitsubishi in order to connect to a S7-1200 PLC. The description of the physical connection (Ethernet) between the GOT1000 and the Profinet Port of the S7-1200 CPU is described in the attached image. It is taken from the following manual, chapter 14.3, which further describes the xcomm settings required, and theaddressing schemes used to connect variables in the S7-1200 to registers in the GOT1000. http://dl.mitsubishielectric.com/dl/fa/document/manual/got/sh080870eng/sh080870engw.pdf If you need further information or help on thos subject, you should search the Mitsubishi site. Hope this helps, Daniel Chartier |