Hi musti463, The first things i spotted is the station name...i would prefer not to put “-” as computer name. Pcs7 is very sensitive to computer name. Take note of this. Can you check your target path in your os? Right click on the os under pc station. Then can you check the access right? Are you able to access to the target station folder? Did you set computer name of your project in host file? C->window->system32->drivers->etc->hosts. Hope it helps. |
Last edited by: JazTai at: 5/23/2018 3:11:57 PMPlease give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to
1 thankful Users |
5/25/2018 7:11 AM | |
Joined: 9/9/2015 Last visit: 4/9/2025 Posts: 732 Rating:
|
Hi musti463, You may refer to this link as well. https://support.industry.siemens.com/cs/ww/en/view/88780011 Hope it helps. |