(0)| 12/4/2018 10:39 AM | |
Posts: 3 Rating:
Hello everyone I want to use a transformer for insulation with a sinamics g120c 1.1Kw Do I have to connect the earth terminal to the core of the transformer or I don't need earth at all? Thank you ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/4/2018 12:25:22 PMNew subject after splitting |
| 12/5/2018 7:07 AM | |
Joined: 10/11/2006 Last visit: 1/21/2026 Posts: 6072 Rating:
Hello, please see the attached connection example (taken from the S120 AC Drive Manual). PE needs always to be connected. If the secondary side of the transformer is in delta connection, all restrictions of an IT line supply apply! |
With best regards, |
| 12/5/2018 9:24 PM | |
Posts: 3 Rating:
Thank you for your help Does this provide enough fault protection? |
| 1/20/2019 11:36 PM | |
Posts: 3 Rating:
What are those restrictions? |
| 1/21/2019 3:08 AM | |
Joined: 1/16/2015 Last visit: 1/16/2026 Posts: 46 Rating:
The magnetic core of the transformer should usually be connected to the ground for safety reasons. |