(0)| 3/16/2019 5:23 AM | |
|
Posts: 5 Rating:
|
Dear Sir, We are using 840 D SL and SINUMERIK MCP483 C key MPI 6FC5203-0AF22-0AA2 WITH 22MM ENMERGENCY PUSHBUTTON KEY PAD. WE ARE FACING PROBLEM WITH MCP- WHEN WE PRESS THE KEY IT WILL REMAIN SELECTED AND BLLINKS EVEN AFTER OTHER KEY IS PRESSED CAN WE USESINUMERIK MCO483C PN 6FC5303-0AF22-0AA1 ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 3/18/2019 7:26:20 AMNew subject after splitting |
|
| 3/19/2019 9:30 AM | |
|
Joined: 1/19/2008 Last visit: 10/20/2025 Posts: 998 Rating:
|
Hi, You can use the profinet MCP but it will have to be be parameterised in OB100. Pee |
| 3/21/2019 3:46 AM | |
|
Posts: 2964 Rating:
|
Hello, Does this problem occurred all of a sudden ? or whether this machine is under commissioning ? any alarms are there in screen ? please check your PLC logic for any errors are there ?
Regards, Prakash |