(0)| 3/8/2021 1:13 PM | |
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
Hello, as everytime, pls find relevant infos with your order number: S7-1500 CPU 1510 spec. Try look for Ethernet/IP protocol support, no support I expect. Profinet is best protocol so you need probbaly look for some other Encoder or connect to maybe Schneider PLC and then somehow exchange data. All depends what is available on Schneider PLC and if you have complete access to it with programming. |
With best regards... |
| 3/8/2021 2:34 PM | |
Hello s100425; You might be interested in the IM 155-6MF HF multi-fieldbus interface module, that allows an ET 200SP system to exchange data over Profinet, Ethernet/IP and Mpdbus TCP. You could use it to interface with your A-B encoder. Have a look at the screenshot below for initial information, and you will find the manual here:
Hope this helps, Daniel Chartier |
| 3/15/2021 12:23 PM | |
Posts: 2 Rating:
Hi! thank you for your help. Do i need a ET200SP CPU to go between the IM and the Schneider or can the IM directly interface with the Schneider without a Siemens CPU? Thank you
| 3/15/2021 4:28 PM | |
Hello s100425; If you open the video file in the following document, it will show you how the IM 155-6 MF is configured (to add I/O modules of the ET 200SP line), parametrized to act as a Ethernet/IP module, and the EDS file generated so it can work with an Ethernet/IP scanner. That should give you a good introduction on how to use this interface module: https://support.industry.siemens.com/cs/ww/en/view/109778898 Hope this helps, Daniel Chartier |