Hello,
|
Eng.Mohamed Ibrahim |
|
5/15/2021 3:51 PM | |
Joined: 3/28/2015 Last visit: 9/12/2025 Posts: 725 Rating:
|
Hello,
|
Eng.Mohamed Ibrahim |
|
5/15/2021 4:05 PM | |
Joined: 3/28/2015 Last visit: 9/12/2025 Posts: 725 Rating:
|
Hello, What is the output type of the transmitter: Passive or active ? -------------------------------------------------------------------------------- The 3 or 4-wires transmitter is an active 4-20mA output. The 2- wires analog input module is an active module. You can't install 2 active components directly in the loop. You need to install the Isolator with passive(sink) output between 3 or 4-wires transmitter and 2- wires analog input module. --------------------------------------------------------------------------------- |
Eng.Mohamed Ibrahim |
|
5/15/2021 4:25 PM | |
Joined: 3/28/2015 Last visit: 9/12/2025 Posts: 725 Rating:
|
Hello, You can set the analog module to be used for 4-wires transmitter ,so you can connect the pressure transmitter to it ( if this is suitable for the other transmitters connected to the module). |
Eng.Mohamed Ibrahim |
|
5/15/2021 8:53 PM | |
Joined: 3/28/2015 Last visit: 9/12/2025 Posts: 725 Rating:
|
Hello,
Why? Please have a look at the attached photo. ------------------------------------------------------------------------------------------------------ The module SM331 has 4 measuring range modules (one per channel group). The measuring range modules can be set to 4 different positions (A, B, C or D). ------------------------------------------------------------------------------------------------------ |
Eng.Mohamed Ibrahim |
|
5/15/2021 9:24 PM | |
Joined: 3/28/2015 Last visit: 9/12/2025 Posts: 725 Rating:
|
Hello,
|
Eng.Mohamed Ibrahim |
|
5/17/2021 8:49 AM | |
Joined: 1/18/2019 Last visit: 3/11/2025 Posts: 82 Rating:
|
Check that diagram, how to connect 2 and 4 wire 4-20ma sensors |