11/16/2016 8:52 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hi, Confugration Control (Option Handling) mean that you can configure the I/O Modules in the PLC Rack, so that not all projected modules must be present. Here are 2 FAQ's for this functionality: https://support.industry.siemens.com/cs/ww/en/view/29430270 https://support.industry.siemens.com/cs/ww/en/view/109481852 Regards |
This contribution was helpful to
2 thankful Users |
11/16/2016 2:59 PM | |
Posts: 25 Rating:
|
Hi, ChristophD, thank you for links. That is exactly what I am trying to do. I will try it again using the prepared library. |
11/22/2016 10:39 AM | |
Joined: 2/27/2014 Last visit: 8/28/2025 Posts: 689 Rating:
|
Hello, See the attached . AttachmentOption.zip (1127 Downloads) |
With Best Regards, |
|
This contribution was helpful to
1 thankful Users |
11/22/2016 1:00 PM | |
Posts: 25 Rating:
|
Hello, DJ_1, your video was very helpful. I found only difference in your configuration: Startup after POWER ON your: "Warm restart - RUN" mine: "Warm restart - Mode before Power off". I changed it, but this did not effect. This is my tested project : link In fact, that is your project with the changed CPU. |
11/22/2016 1:16 PM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
Hello, which value have the STATUS of the "OH_CONFIG_CTRL"? Christoph |
11/22/2016 1:45 PM | |
Posts: 25 Rating:
|
Hello, The status of OH CONFIG_CTRL (and of included WRREC) is #C0B0_B800 (DP slave or module reports an invalid parameter). |
8/5/2021 12:40 AM | |
Joined: 3/16/2015 Last visit: 10/10/2021 Posts: 1250 Rating:
|
Have a look at this, it may be helpful. Note that the project is attached at the bottom so you may want to download it first and then go through the article. |