5/26/2014 1:20 PM | |
Posts: 205 Rating:
|
Dear Expert, Is it Possible to communicate between any two SIEMENSE HMI to HMI??? no other master device like PLC,SCada.... |
5/26/2014 1:58 PM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating:
|
Hi! Not sure this configuration even possible. |
5/26/2014 2:31 PM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Practically is not possible. Always should have "something" between both HMIs. |
5/26/2014 2:33 PM | |
Joined: 6/8/2013 Last visit: 6/24/2025 Posts: 159 Rating:
|
Hi, As per my knowledge direct HMI to HMI communiation is not possible but if using OPC it may be possible. |
5/26/2014 4:04 PM | |
Joined: 10/10/2010 Last visit: 7/5/2025 Posts: 309 Rating:
|
you can use a master controller PLC to communicate with the two hmi |
5/26/2014 4:14 PM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, Is it a real or Hypothetical question? If you would like to communicate between 2 HMI stations, then we have two options:
This because HMI doesn't have an internal memory to transmit from or to. You write on HMI an Input field for instance to write it in certain address of the CPU or you can read this address from PLC on HMI output field. So, the question is not HMI-HMI communication coz there should be CPUs in the system. Back to above options:
Hope this helps. |
Ayman Elotaify |
|