9/14/2012 8:00 AM | |
Posts: 303 Rating:
|
Dear all, Can any one give sample program for highspeedcounter for the CPU 313-C (6ES7313-5BE01-0AB0).
|
9/14/2012 8:32 AM | |
Posts: 303 Rating:
|
Just i am practising. |
9/14/2012 8:51 AM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, O.k. so lets start with how to call the counter block, in the attachment the counter is used for positioning. Regards, Marcjan AttachmentFC11-count.pdf (229 Downloads) |
Last edited by: Marcjan at: 9/14/2012 8:53 AMProblem solved? |
|
9/14/2012 8:53 AM | |
Posts: 303 Rating:
|
I didn't find any attachment. |
9/14/2012 9:12 AM | |
Posts: 303 Rating:
|
Please check the attachment. How can give signal to the I0.0. Can you please upload the complete program.
|
Last edited by: Saradhi at: 9/14/2012 9:13 AM |
|
9/14/2012 10:58 AM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Please use the Default adresses in your hardware config, it's only confusing you. The physical hardware inputs don't change by changing the adresses. In this manual you can read how to setup a counter. The sample projects Regards, Marcjan |
Problem solved? |
|
9/15/2012 8:08 AM | |
Posts: 303 Rating:
|
Thank You. Solved. |