10/5/2023 7:51 PM | |
Posts: 13 Rating:
|
I have the 6ED10521MD080BA1 From what I have read, the Logo is unable to use a 2 wire analog input, and must instead use a 3 wire sensor. |
10/5/2023 8:13 PM | |
Joined: 12/18/2014 Last visit: 9/17/2025 Posts: 35967 Rating:
|
Please upload your program as a ZIP file. It's better to work with the original diagram as with a screenshot. |
10/5/2023 8:16 PM | |
Posts: 13 Rating:
|
Try this one
AttachmentRepeating Loop with 2 limits and start stop.zip (343 Downloads) |
10/5/2023 8:43 PM | |
Posts: 13 Rating:
|
How would you recommend fixing that issue? |
10/6/2023 1:27 PM | |
Posts: 13 Rating:
|
Do you see any issues with this program?
AttachmentRepeating Loop with 2 limits start stop and safeties.zip (349 Downloads) |
10/6/2023 2:10 PM | |
Posts: 13 Rating:
|
Try this one. If both limit switches are activated at the same time (one sticks and the other is activated) then it stops. If the cylinder does not extend in the set amount of time, activating the limit switch, it stops.
AttachmentRepeating Loop with 2 limits start stop and safeties V2.zip (418 Downloads) |
10/6/2023 3:52 PM | |
Joined: 12/18/2014 Last visit: 9/17/2025 Posts: 35967 Rating:
|
Try this. You must chance the timer values and the number of loops to your wish. AttachmentRepeating Loop with 2 limits start stop and safeties_V2.zip (357 Downloads) |
10/9/2023 2:35 PM | |
Posts: 13 Rating:
|
Unless I am missing something, the maximum time for step 2 times out regardless if Limit Switch 1 is activated. |
10/9/2023 5:30 PM | |
Joined: 12/18/2014 Last visit: 9/17/2025 Posts: 35967 Rating:
|
I made a little chance, try this.
AttachmentRepeating Loop with 2 limits start stop and safeties_V3.zip (375 Downloads) |