8/10/2024 6:54 AM | |
Joined: 12/18/2014 Last visit: 9/16/2025 Posts: 35965 Rating:
|
Who set M1 to high? A remote device? |
8/10/2024 8:05 AM | |
Posts: 11 Rating:
|
That's right. I use Modbus TCP and send the value 1 to M1 using Modbus Poll. |
8/10/2024 10:46 AM | |
Joined: 12/18/2014 Last visit: 9/16/2025 Posts: 35965 Rating:
|
It's the problem as in this topic? make PLC retain the last value it read from the slave |
8/12/2024 5:15 AM | |
Joined: 9/11/2014 Last visit: 9/16/2025 Posts: 868 Rating:
|
Hi, a LOGO! 8.4 has an additional retentive memory rage (VRx). This can be used to solve such RQ. |
8/12/2024 3:20 PM | |
Joined: 12/18/2014 Last visit: 9/16/2025 Posts: 35965 Rating:
|
I see it the same way as the user gwazee. I carried out a small test. To do this, I transferred the MB0 of a remote LOGO! to the VRB0 of the LOGO! 8.4. What is the point of the remanence then? AttachmentScreencast 2024-08-12 16-36-23.zip (404 Downloads) |
Last edited by: ixo65 at: 08/12/2024 15:21:44 |
|
8/13/2024 5:32 AM | |
Joined: 9/11/2014 Last visit: 9/16/2025 Posts: 868 Rating:
|
Hi, I have used the attached program for testing with a LOGO! 8.4: I have set both bits to "1" in online test. Then I have done a power cycle at the LOGO! 8.4. Here the result after the power cycle and restart of the online test: VR0.0 has still "1" signal, V0.0 "lost" "1" signal. So remanenz via VR in a LOGO! 8.4 should work as long as no other device activilly change the state of VR0.0. AttachmentVR0_0 Test.zip (409 Downloads) |
Last edited by: AutoGen_380038 at: 08/13/2024 05:36:56 |
|