4/24/2016 5:52 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, Are you sure that in the Hardware setting of TIA, you put the right part number of CPU? As your provided CPU Part Number is not released for TIA! If you look at programming software in the technical specification of the CPU "6ES7315-6FF04-0AB0" , you will found the following data: STEP 7 V5.5 + SP1 or higher or STEP7 V5.2 + SP1 or higher with HSP 218 + Distributed Safety And for HMI, MP377 can be configured using WinCC flexible. I don't think that you can configure it using WinCC TIA. Am I right? |
Ayman Elotaify |
|
4/26/2016 11:20 AM | |
Joined: 8/5/2010 Last visit: 8/4/2025 Posts: 17 Rating:
|
Dear Ayman, I'm pretty sure that he has used TIA V11, regards,
Francesco |
4/27/2016 2:37 PM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, Then the Panel is working and may be the TIA project is corrupted. You can ask the supplier to send you another project or even "Pack&Go" file to download directly to the MP. May be the problem happen when you tried to edit something in V12 and the main project created in V11. "Pack&Go" is a good solution if you don't want to open the project and make edits in it. The programmer can generate Pack&go file using WinCC flexible or WinCC TIA. How do you transfer a WinCC flexible configuration without configuration software to an operator panel (Pack&Go)? |
Ayman Elotaify |
|