11/26/2020 5:36 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878) |
Hello, Please check the setting of mode selector & selection of enable signals in mode selector is correctly set. Please refer attachment for more information. If above setting is OK & you want to ensure independent control in modes, you need to write logic using logic functions configuring mode selector as inputs. AttachmentSIMOCODE pro mode selector.pdf (885 Downloads) |
Last edited by: PISCEAN 2010 at: 11/26/2020 06:00:21 |
|
11/26/2020 7:44 AM | |
Posts: 39 Rating: (0) |
Hello Thanks for your answer. I have read your PDF and i think all settings in my Simocode are correct ,please look at my screenshots. When S1 and S2 are high it is remote control and when S1 is high and S2 is low it is local control. To set S1 I'm using ' fixed level 1 ' so S1 is still high. I only change S2 by 'input 2' and the input is connected to switch button. Attachmentsimocode.pdf (784 Downloads) |
11/30/2020 7:35 AM | |
Posts: 39 Rating: (0) |
Hello, Thanks for your answer! It was helpful and I have done own logic tables now everything works fine. |
This contribution was helpful to1 thankful Users |