Hello Andrew_097 The signal „<Axis>.ActorMonitoring.Power“ depends on the drive state “S4: Operation” (bits 0,1,2 in <Axis>.driveda.zsw[0] must be “1”). To find out where the time get lost you must trace the status word and the control word of the drive (“<Axis>.driveda.zsw[0]” and “<Axis>.driveda.stw[0]”). You can verify the states with the description of the “Sequence control”. The “Sequence control” for Sinamics S120 is to find in chapter 2.10 of the following document: http://support.automation.siemens.com/WW/view/en/29217393 Regards ThomasD |