Hello, Should be no problem to replace these TD's. However if the TD parameters are changed(not default) you have a problem. If the device does not work you may need to change the TD addres and/or parameterblock offset. So a backup from plc program may help then. S7-200 SIMATIC Text Display (TD) User Manual Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to2 thankful Users |
11/11/2014 7:33 AM | |
Joined: 4/22/2010 Last visit: 11/15/2024 Posts: 5697 Rating: (715)
|
Hello, The only problem you may face is that you can't upload the program in case your microwin version is older than the version the PLC is programmed with. No risk that the PLC will stop working, be sure you hit the right button (upload) if you hit download you transfer an empty program to the PLC. By the way it's better to upgrade your Microwin version, there is a lot written about CN PLC's and older Microwin versions. The latest version SP8 or 9 can handle older programs, except the ones written in a dos version. STEP 7 MicroWIN V4.0 SP8 and SP9 - Available for Download If you have trouble to upload the PLC please search for CN threads for some tips. regards, Marcjan |
Last edited by: Marcjan at: 11/11/2014 7:36 AMProblem solved? |
|
This contribution was helpful to1 thankful Users |