10/16/2024 5:45 AM | |
Joined: 10/11/2006 Last visit: 11/14/2024 Posts: 5941 Rating: (816)
|
Hello, please refer to the Masterdrives catalogue note: "The DC bus must be in a de-energized state when inverters or braking units are switched in or out." If this is not the case and no external pre charging circuit for the DC link capacity exists, fuses blow or even the inverter itself can be destroyed by direct switching to a charged DC link. To get more information, you could also refer to the application note for SINAMICS S120 regarding that topic. AttachmentMasterdrives - DC connection.pdf (53 Downloads) |
With best regards, |
|
This contribution was helpful to1 thankful Users |
10/16/2024 9:21 AM | |
Joined: 3/6/2022 Last visit: 10/23/2024 Posts: 107 Rating: (2) |
Ok. As far as I understand it this is how it works. When I connected the inverter to the already live DC bus it supplied maximum power to the inverter and there was an inrush current because the DC bus tries to charge the inverter's capacitors almost instantly. But if the rectifier is turned off first to deactivate the DC bus and then the inverter is connected to the bus and then the rectifier is turned on the inverter fuse won't blow because the rectifier will gradually charge the inverter's capacitors through its own inbuilt pre-charging circuit and limit the current. Am I understanding it right? |