3/24/2025 8:06 AM | |
Joined: 10/21/2024 Last visit: 7/17/2025 Posts: 13 Rating:
|
Here is my program. I belive something is wrong with VW addresses. See next post.
AttachmentModbustest.zip (200 Downloads) |
3/24/2025 8:28 AM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
In the Modbus connection table have the entries: VW0 - 2 Words - HR1 - 2 Words With the first entry writes write you VW0 and VW2 to HR1 and HR2. An Holding Register is a Word (16 Bit). But the addressing of HR and VW are different. Example: HR1, HR2, HR3, HR4 and so on ... AttachmentLOGO! Bit, Byte, Word and DWord.pdf (261 Downloads) |
3/24/2025 9:06 AM | |
Joined: 10/21/2024 Last visit: 7/17/2025 Posts: 13 Rating:
|
Thats the configuration of the modbus relais. |
3/24/2025 11:29 AM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
Can you show me a screenshot of the Modbus Poll when you switching on the relay? |
3/24/2025 11:41 AM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
Try this ... |
This contribution was helpful to
2 thankful Users |
3/24/2025 1:21 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
That sounds good ... |