Hi. Check your PAC3200 communication settings for"Modbus TCP" protocoll in your device (page 21.6) |
4/26/2012 4:13 PM | |
Posts: 3093 Rating: (323) |
Hello dtv, the client must use remote port 502 and the UNIT must not be 0. Regards, Kaulquappe |