Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello jeet2907 You can assign the following signals to a configurable Output Module attached to a 3WL BreakerCubicle Bus : Overload (L) Short-time-delay short-circuit (S) Instantaneous short-circuit (I) Ground fault (G) Overload in neutral conductor Phase unbalance - current Phase unbalance - voltage Under frequency Over frequency Under voltage Over voltage Active power in normal direction Active power in reverse direction Total harmonic distortion - current Total harmonic distortion - voltage Reversal of phase rotation direction Pl see attachment. We have used this functionality alongwith COM15 Profibus Module. Here are the Links to the SENTRON Communinication Manuals for your reference : System manual for 3WL/3VL circuit breakers with communication capability - PROFIBUS System manual for 3WL/3VL circuit breakers with communication capability - Modbus Hope this Helps Cheers Navnag AttachmentSENTRON_Configurable_Outputs.pdf (359 Downloads) |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
5/21/2014 7:59 AM | |
Posts: 235 Rating: (52) |
Dear Navnag First of all thanking you lot for your reply,its realy a good infirmation for me my vedor is also suggested same to me, but this COM 15/16 facility available only with ETU 45B and ETU 76.Now i have only 1 AcB with ETU 45B while other 11 ACB with ETU 37B so now how can i got feedback for another 11 ACB.If there is another option for the same then pls provide you feedback. Waiting for your reply Thanks & regards |
5/21/2014 9:07 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Dear jeet2907 It is not a must to have COM 15 / COM 16 to use Cubicle Bus Modules. Pl see attachment regarding how to connect Cubicle Bus Modules without COM 15 / COM 16. Of course some of the options are not available if a COM 15 / COM 16 is not used. ( Pl read the manual for details ) You needACBs with ETU45B and above have built in cubicle bus. However it is possible to retrofit the ACBs without Cubicle bus at site to ETUs with CUbicle Bus. Pl speak to your Siemens Contact about this. You will also need BDA ( Breaker Data Adapter) to configure the ETU and Cubicle Bus Modules if there is no COM 15. ( WIth COM 15 you can configure through Profibus using Switch ES Power ) Hope this helps Cheers Navnag AttachmentConnecting_Cubicle_Bus_Without_COM15.pdf (368 Downloads) |
There is no such thing as the last bug in a program |
|