7/1/2013 1:50 PM | |
Posts: 43 Rating: (9) |
Dear Expert, If I m going to select 3WL ACB with 4000A & I want spring charge indication, then pls suggest for wiring scheme & terminal connection of ACB.
|
7/1/2013 9:19 PM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477) |
Look at Configuration Manual SENTRON 3WL Air Circuit Breaker On Page 49, you will find connection diagram Connect accordingly Hope this will help you Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/2/2013 6:53 AM | |
Posts: 1064 Rating: (72) |
check pg 49 of the manual connector x7 terminals 10 and 11 |
This contribution was helpful to1 thankful Users |
7/2/2013 6:59 AM | |
Posts: 1064 Rating: (72) |
sorry i didn't see you mention page number |
This contribution was helpful to1 thankful Users |
7/10/2013 1:24 PM | |
Posts: 235 Rating: (52) |
Attachmentspring charge indication.pdf (492 Downloads) |
7/10/2013 1:42 PM | |
Joined: 11/21/2007 Last visit: 7/7/2024 Posts: 2325 Rating: (307) |
Hello S20 ( As the name says ) is a "Ready to Close" Contact and cannot be used for "Spring Charged" You need to use S21 ( Available on Trip X7 Terminal No 10-11 ) - Pl see Attached Wiring. As already mentioned this terminal is not available if COM 15 / COM-16 is installed Hope this helps Cheers Navnag AttachmentSENTRON_Wiring.pdf (460 Downloads) |
There is no such thing as the last bug in a program |
|
Follow us on