Dear All, I have encountered the following problem: I've mounted the Profibus DP module (7KM9300-0AB01-0AA0) on a SENTRON PAC3220. Since then the sentron pac3220 does not measure the voltage/current values and shows me on the display: System Message 007 UIP Task. Did anyone have the same issue? Can the problem be solved somehow? Thank you. Kind regards, Endre Katona |
This contribution was helpful to2 thankful Users |
4/14/2023 5:52 AM | |
Joined: 7/22/2021 Last visit: 5/23/2023 Posts: 1 Rating: (0) |
Did u solve the problem? I have the same Problem
|
9/6/2023 8:19 AM | |
Joined: 7/13/2021 Last visit: 10/9/2024 Posts: 3 Rating: (1) |
Good morning to all, so after some talk with Siemens HW support, testing and trying to get the device PAC3220 to live it was concluded and recommended by Siemens HW support "claim the device". It seams it is issue of the PAC3220 device itself and not of the ProfiBus DP module, as far I was able to go. It was concluded in our case that the ethernet ports on the PAC are not communicating, the green and orange LEDs on the ethernet ports shine all the time - does not matter if the ethernet cable is connected or not. It was recommended to run diagnostic of the PAC by powerconfig - commissioning and service software. The powerconfig is able to scan the selected ethernet network without defining subnet to scan, it is able to find device with factory default IP address 0.0.0.0 and initiate communication with it. Tested on other well working PAC3220. To modify the configuration of the PAC3220 from the powerconfig you have to unlock the hardware write protection key on the PAC.
NOTE2: The flashing notification "System message: 007, UIP Task" on the PAC screen, frequency approx 2 seconds, will kick you back on main screen, so you are not able to get to the relevant level of the setting menu to check or modify something. That is quite sad due the device seams responsive, just the notification blocks the interaction with it. NOTE3: Any external moduls or whatever physical manipulation with the device has to be done without power supply, see manual, assume the connection of the modules can cause some short circuit on the board, or something like that. NOTE4: The set ProfiBus DP address is saved in the momeory of the ProfiBus DP module, so in case new ProfiBus DP module is inserted the configuration through - PAC setting menu OR powerconfig - has to be done. Details about devices: So good luck to others with similar issue, Bolek |
Last edited by: Jen_Moderator at: 09/29/2023 10:05:24Link optimized. |
|
This contribution was helpful to1 thankful Users |
6/6/2024 4:27 AM | |
Joined: 8/2/2023 Last visit: 6/6/2024 Posts: 2 Rating: (2) |
Hello everyone, I am also having the same problem, someone please help me how to fix this error. |