Hi, 1. Is the name of the server computer in the WinCC project also the name of the computer on which the WinCC project is currently open? -> open the server computer with a double-click in the WinCC Explorer. If the "Accept local computer name" button is grayed out in the General tab, both names are identical. 2. Is the project really a multi-user project? -> Right-click the project name and select properties in the WinCC Explorer. The project type must be set to multi-user project in the General tab. Please check that the change was applied correctly. 3. If 1st and 2nd do not help, the .mcp file must be recreated. Please see: How do you replace a defective ".mcp" file? The computer can then be created again. |
A rating will be well appreciated. |
|
This contribution was helpful to
2 thankful Users |
11/19/2024 12:22 PM | |
Joined: 8/19/2021 Last visit: 4/29/2025 Posts: 21 Rating:
|
The third option solved the problem. Thank you! |