Joined: 9/27/2006 Last visit: 11/2/2024 Posts: 12292 Rating: (2690) |
Hello Shambo; This error apears when you try to access a non-existing address, in the I/O mapping, in the DBs or in block calls. You should have more entries in the diagnostic buffer that should help you identify the type opf error and the misfit address (especially if OB121 is loaded in the CPU). Look at the following FAQ for more details: http://support.automation.siemens.com/WW/view/en/23151678 Hope this helps, Daniel Chartier |
2/25/2008 2:25 PM | |
Posts: 11 Rating: (0) |
Thanks for your Help Daniel. Its really help me a lot........... |