can we use 3ru1146-4jb1 for dc motor 440vdc/48amp ? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 9/13/2015 3:37:12 PMNew subject after splitting |
|
4/25/2016 8:36 AM | |
Joined: 3/17/2013 Last visit: 8/25/2024 Posts: 481 Rating: (43) |
Not sure for DC voltages, Data sheet mentioned for AC3 only even though current wise 48 A comes in the range Vijay Attachment3RU1146-4JB1.pdf (923 Downloads) |
4/25/2016 9:13 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Yes but remember to connect all 3 poles in series. Please refer the attached extracts from SIRUS system manual for LV switch gear. |