6/10/2008 1:14 PM | |
Posts: 27 Rating: (0) |
Hello, I have alarm 6 on the simodrive when i try to start to move the "x"axis...what does it mean? it is possible to have the alarm list? thank you Marco Gualengi |
6/10/2008 11:28 PM | |
Posts: 271 Rating: (29) |
Hello Marcus, The part number you give is for the Power Module. The alarm #6 is located on the control unit which probably starts with the part number 6SN1118-xxxxx-xxxx. If you have a feed drive controller for 1FT5 motors, alarm #6 is indicating that the speed controller is at end stop. This means that the motor either does not turn when it's enabled or that the current output of the drive is going to its limit and stays there for too long. The drive is protecting itself from damage. Details for other controllers can be sound in the Simodrive folder at www.automation.siemens.com/doconweb. Open the Simodrive 611 Analog Start Up Guide. Hope this helps... |
Follow us on