9/17/2011 7:54 PM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating: (113) |
You have invert the R(eset) input of the RS Block (B001) Its only works if I2 is always ON. The R(reset) on the RS laching Block has more prio than the S(set) Thus when Set AND Reset both are 1 the output is 0 Nex time, you make a .zip of your programm, and post it here, so we kan test it. Look at the attachment AttachmentRS-Display.zip (307 Downloads) |
9/17/2011 10:41 PM | |
Posts: 2 Rating: (0) |
Hi, Yes, it is correct that I have inverted the I2 input since my stop button is NC. Problem is that when I simulate the program in LSC everything work as it should. It's not before I have downloaded the program to the LOGO itself, the problem appear. regards, Jon AttachmentCircuit Diagram2.zip (290 Downloads) |
9/18/2011 7:24 PM | |
Joined: 9/6/2008 Last visit: 3/29/2024 Posts: 134 Rating: (16) |
you have to change the properties off the input I2 ,from switch ( make contakt ) to push button AttachmentRS DISPLAY.zip (312 Downloads) |
http://electrotech-techblogg.blogspot.gr/ |
|
Follow us on