Hello ALAND00 In a TIA Portal Project there are no WinCC flexible project files! so you cannot generate a WinCC flexible Project out of a TIA Portal Project, and this is also not your problem in this case. First of all you can do a Backup and Restore if the original Panel does still work : https://support.industry.siemens.com/cs/ww/en/view/28928853 If you can do a ping to the panel then a downlaod should be possible. set the transfermode in the Panel to Ethernet and start the Transfer mode. Then use in the extended dowload to device in TIA Portal also Ethernet and use "devices with same addresses" If you have trouble with that, then I think on the Panel is a different Image than in TIA selected. In this case check which Image Version is installed in the Panel (you can see in Control Panel). If there is still an old WinCc flexible Image on the device you have to do a OS Update or even better a Reset to factory settings with Prosave and to load the TIA V13 Image (or V12 there are no newer Images thatn V12 for these kind of Panels in TIA available) Bye Murof |