Hi, as far as I know snap7 is based on s7-communication protocol. Is the access granted in the plc hw configuration? Depending on which PLC (and also which spefic firmware) the access via s7-communication has to be granted seperately. There should be an option in hw configuration like "allow PUT/GET access..." which does mean s7-communication. ***EDIT*** Restriction of communication services-> activate the "Permit access with PUT/GET communication from remote partners" option Event its called PUT/GET, this means S7-communication protocol in general. Maybe its worth a try to check. regards sancruz |