4/29/2020 1:59 PM | |
Posts: 2964 Rating:
|
Hello, It is nothing to do with the DIP switching setting at present.
|
5/8/2020 3:17 PM | |
Posts: 28 Rating:
|
Hello, i ve still receive the power supply alarm eventhought i have switch the profibus cable in the attachment. Any ideas please? |
5/16/2020 6:15 PM | |
Joined: 10/17/2007 Last visit: 9/15/2025 Posts: 4452 Rating:
|
Hi, your topic has been more than 3 weeks, now it's time to find out root cause #1--Any of error on the 611U drive such as 599 or 608 , Siemens will call them drive error /fault, "Power supply Malfunction" is not good description --it is machine builder made one #2--error 608 means drive getting commandant to move the motor, but motor not moving for some reason--as Ekalavya already guided you to check many items, I suggest --if you never touch/ change parameters, you need only check hardware related issues--such as motor, motor power cable,contractor--if bestrewn drive module out put to the motor there is contractor? also check mechanical blocking from electrical drawing you should know 1st drive B axis is Y axis or spindle If outside HW checking all good, think about drive module defective
|
Last edited by: nulizhang at: 05/16/2020 19:35:43Check HW If you like my comments please |
|