7/5/2013 12:19 PM | |
Posts: 202 Rating:
|
Hi Ste39 It means i have to go for that OLR which is 50% to that of the motor
|
7/16/2013 12:34 PM | |||||||
Posts: 39 Rating:
|
|
||||||
7/17/2013 7:13 AM | |
Posts: 235 Rating:
|
No dear in star delta we mounting OLR in phase current(mounting OLR exectly below to the main contactor),we can also put OLR in line current but we cant do that bcoz the main reason of money saving.If we put OLR in with line current (or say above the main contactor )we require relay range similar to the FLC so its higher rating and its cost is more than halved rating.Its a main reason to put OLR in phase current. For your refrence please find the attach sheet of star-delta wiring drg and control too.
Attachmentstra-delta scheme.pdf (979 Downloads) |
Last edited by: jeet2907 at: 7/17/2013 7:13 AM |
|
This contribution was helpful to
1 thankful Users |
7/17/2013 10:46 AM | |
Posts: 202 Rating:
|
Hi there Does the Line current or Phase effects the mounting or rating of OLR??? please explain....
|
Follow us on