5/12/2014 12:19 PM | |
Posts: 235 Rating: (52) |
Dear expert, I am used ACB ETU with LSING protection, now i want to bypass NG protection from the same. so plesae suggest me can i do? if yes then how? |
5/12/2014 1:22 PM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878) |
Yes. You need to disconnect CT of neutral conductor. |
This contribution was helpful to1 thankful Users |
5/13/2014 8:48 AM | |
Posts: 235 Rating: (52) |
Dear PISCEAN Thanks for the reply,but its not possible when the power supply is on. yestrday i was referd the catalog of ACB and found that this fcility available in some ETU to switch on and off for the same. |
This contribution was helpful to1 thankful Users |
5/14/2014 7:49 AM | |
Posts: 202 Rating: (16) |
DearPISCEAN 2010 As the CT are in built & internally connected is it appropriate to disconnect the CT aslo if we do it from our end wont it void the warranty. I would a I^2t operation for the bypass of all the protection
|
5/14/2014 7:57 AM | |
Posts: 202 Rating: (16) |
Dear Indrajit You can bypass any protection of the ACB using the knob provided on the ACB. Please find the attached Image file for the same.
|
5/14/2014 8:42 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878) |
Hello, Neutral CT is optional accessory. You can disconnect it easily or simply bypass the neutral buss. |
5/15/2014 11:09 AM | |
Posts: 235 Rating: (52) |
Dear piscean2010, Sorry but Neutral CT is not an optional accessory( not need to order seperatly) for 4P ACB, It must come with ETU proction ACB,and its mountong at such a way where we can not diconnect it easily. But if we want to bypass NG protection then this facility available with such a ETU in which you can Swith ON/OFF the same.For more detailed you can refer the ACB catalog. |