hi,
is there anything loaded on the CPU? you need to load a valid HW-configuration and a program to the CPU. regards, |
FCK WAR! |
|
10/31/2016 9:33 AM | |
Joined: 5/12/2006 Last visit: 11/18/2024 Posts: 22453 Rating: (3030) |
Hi, HW Config should be loaded because the Opton handling is enabled, this is only possible with a loaded HWConfig. But if this Option is active you need a program in the startup to activate a valid data set for Option handling. If you need no option handling deactivate the option in the PLC Porperties and download the Project to the plc.
Christoph |
This contribution was helpful to4 thankful Users |
6/28/2021 8:11 AM | |
Joined: 10/22/2013 Last visit: 9/4/2024 Posts: 8 Rating: (4) |
In PLC properties/Configuration control, the tick mark in "Allow to reconfigure the device via the user program" must be removed. |