10/11/2022 9:57 PM | |
Joined: 1/6/2015 Last visit: 4/2/2025 Posts: 6 Rating:
|
I have had success in the past connecting to G120's on a DP network via ETH. Now I am attempting the same thing with S110s but the only difference is the PLC address is being routed through an S615 Router. No success so far. Source IP 10.232.192.39(615) Destination 10.2.13.234/PLC Not sure why its not working. Would like someone to help me check all the settings. UPDATE: Issue solved. On the Device Address tab where the Profibus Address is specified the white field next to "ADDRESS IN STEP 7" has to have an address which matches it. Unless theres something I do not understand I am not sure what the point is of having that field to fill in if its an exact match. Attachment2022-10-08 23_58_20-STARTER - PSA - [S110_CU305_DP_ROTATE - Commiss. interface].png (707 Downloads) |
Last edited by: LostinTX at: 10/13/2022 07:07:00Last edited by: LostinTX at: 10/21/2022 07:05:01 |
|
10/21/2022 6:59 AM | |
Joined: 1/6/2015 Last visit: 4/2/2025 Posts: 6 Rating:
|
I tried that. Siemens support helped me find the answer which was right in front of my face! |