(0)| 3/18/2023 10:04 AM | |
|
Posts: 30 Rating:
|
Dear experts,\ We have Sinamics S120 drive for application of wagon tippler,recently our drive was tripped in Fault 30022 and Found IGBTs are failed and all fuses are Blowen. We analyzed condition and found that drive was tripped in motor stall fault in the past 2 time before this incident.Encoder signals are not heathy in the trends. In analysis the motor current was gone upto 900A, even though limit is 605A(p640). Questions: 1.Why the drive was not tripped when encoder failed? 2.Why the current was shoot up even we have limited to 605A? 3.Why drive not tripped in speed mismatch of both master and slave drive? What can be done to avoid this in future? Expert parameter list is attached for reference. AttachmentExpert list_WT1_M2.xlsx (544 Downloads) |
| 3/18/2023 11:11 AM | |
|
Posts: 8092 Rating:
|
Hello Ajay, Can you provide master drive parameter list & connected motor nameplate snap? |
| 3/19/2023 3:51 AM | |
|
Posts: 30 Rating:
|
Please find the attached Master drive expert list.(M1). Motor name plate data is same as in P304 - P311 AttachmentComplete_details.zip (574 Downloads) |
Last edited by: Ajay5 at: 03/19/2023 03:53:48 |
|
| 3/23/2023 4:21 AM | |
|
Posts: 30 Rating:
|
Thanks for your reply, As you rightly mentioned the drive is designed for 150% of current for 60sec,which is as our operational requirement.being a wagon tippler(twin wagon) the drive is designed for 150% loading for 45sec during the load tilting of wagon. We were analysing the issue and following observation: 1.When encoder feedback is zero,then the drive is tripping with stall or blocked rotor fault.-- statement mentioned in manual is conflicting with our trends,can you please provide any logic description to stall or blocked rotor. 2.During failure follower motor current went upto 900A for 45msec,at the same time master has limited the current at 605A,as both machines are hard coupled and seeing the same load,as per my opinion current shoot is not due to load,else it has to be replicated in both machines. 3,We replaced motor module of follower machine and Did local trail and found still the current was shooted upto 900A for follower motor and speed was 0.however same time master was limiting the current at 605A.(immediately we stoped the machine to prevent failure). 4.After that we replaced encoder also for follower motor and trail taken and found current was normal and both machines are in sync and normal in operation. We have the following queries in our mind: 1.Is there any possibility that current controller is not working properly,if encoder feedback is missing/malfunctioning (any parameter need to be alter to limit the current on this condition). 2.Is there any possbility that we can trip the drive with speed mismatch/encoder error fault in case of encoder failure. As you mentioned drive was running from last 9 years and purchased on 2012. can you please provide us any preventive maintenace replacement chart for all the componenets,so that we can preventively replace components to prevent failure. AttachmentWagon_drive.zip (553 Downloads) |
Last edited by: Jen_Moderator at: 03/31/2023 09:47:42Text formatting optimized. |
|