Hello, I have a similar question. Can a SIEMENS ET200SP (IM155-6PN ST) be configured as a standalone I/O drop for use/access via a GE (Emerson) RX3i (CPE305) that has a Profinet Controller (PNC001)? They should be PROFINET compatible. I've tried the available GSD files and NONE appear to work. If the ET200SP needs to be PRE-configured in TIA, how is this accomplished WITHOUT an S7 CPU? Any advice is appreciated. Thanks. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/27/2023 11:57:32New subject after splitting |
|
4/27/2023 12:09 PM | |
Joined: 7/9/2015 Last visit: 6/27/2024 Posts: 3859 Rating: (567)
|
Hi, you need GSD files from this entry: PROFINET GSD files: I/O - ET 200SPCheck the supported GSDML Scheme of your Tool. So use under some circumstances an older scheme. Regards, Towome |
|
|