Hi, You may check with the Primary Setup Tool the connection, then you don't need other software and you can check then directly if there is a problem with STEP7. [:P] The PST-Tool is to find on the Siemens Portal: Primary Setup Tool (PST) Version V3.1 Adress Setting of SIMATIC NET Industrial Ethernet Products - no functional change opposite version 3.1. http://support.automation.siemens.com/WW/view/en/19440762 Please consider you have first off all have to install the "DLC-Protocol", see the description in the link mentioned here before. DLC Protocol (Windows XPProfessional) The DLC protocol must be installed separately for Windows XP, because it is not included in the scope of supply of the operating system. The necessary files are located in the sub-directory "DLC Protocol" in the PST installation directory. Please proceed as follows: |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|