(0)| 11/11/2010 12:45 PM | |
|
Joined: 3/21/2006 Last visit: 10/16/2025 Posts: 10239 Rating:
|
More details at Data Communication via Modbus/TCP with S7-1200 (CE-X22) BR, Hristo Mihalev |
| 11/15/2010 8:50 AM | |
|
Joined: 10/7/2005 Last visit: 12/19/2025 Posts: 3052 Rating:
|
The 1200should indeed be able to communicate with up to 8 PAC3200's at the same time as per technical spec of the 1200 manual and THIS FAQ (Modbus on TCP will use the T-Blocks related TCP connection even though the Example does not seem to explicitly state this). |
|
Cheers |
|
This contribution was helpful to
|
|
| 11/15/2010 2:09 PM | |
|
Joined: 7/7/2010 Last visit: 12/23/2025 Posts: 16325 Rating:
|
Thanks! I am very glad to know this. |
|
science guy |
|
This contribution was helpful to
|
|
Follow us on