7/13/2011 10:28 AM | |
Joined: 4/19/2008 Last visit: 9/3/2024 Posts: 1525 Rating: (159) |
Hi Patil, You can't used the CP341 on the UR2 H Rack, You have to used the ET200M, IM153-2 INTERFACE REDUND.BUNDLE on next to this IM you can mount the CP341........ you have to used the Active Bus Module. hope you have got the solution .....what you looking for .... |
Last edited by: Ammy at: 7/13/2011 10:31 AMAmmy |
|
This contribution was helpful to1 thankful Users |
7/13/2011 11:56 AM | |
Joined: 8/18/2009 Last visit: 6/17/2024 Posts: 548 Rating: (33) |
Dear Ammy, is it must to used the Active Bus Module for CP 341 with IM 153-2. |
Rajkiran Patil |
|
7/13/2011 12:32 PM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839) |
Hello, Yes. You have to use the active bus module for your case. You have a fault tollerent system, so you have two different buses. And so, you have to use two different IM153-2. One for each bus. If you ordered the Red bundle6ES7153-2AR03-0XA0as mentioned by Ammy, you will recieve two IM153-2 with one bus module IM/IM. In this case you will save some mony as the price of Red bundle is approxmitlly double price of IM153-2, So, you will save the price of bus module IM/IM in case of ordering it separitlly. And you have to use the ET200M rack with function insert/remove. For CP341, use Bus Unit6ES7195-7HB00-0XA0 Hope this helps.
|
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
Follow us on