Hello; You have a few choices if you need to program diagnostics of failed Profibus slaves in your project. Here are 2: -Using SFC13 "DPNRM_DG" in OB82 (Diagnostic Interrupt OB): this FAQ has a downloadable project that you can use as a basis for your own blocks: http://support.automation.siemens.com/WW/view/en/2190197 -Using Profibus-DP diagnostic functions FC125/FB125, that you can download here: http://support.automation.siemens.com/WW/view/en/387257 Hope this helps, Daniel Chartier |
5/26/2008 9:46 AM | |
Posts: 2348 Rating: (264) |
You can also choose SFC51 with ID xx92 to perform fast (but not as full as in SFC13) slave diagnostics. |