How are you all I have redundant system S7-400H with redundant cpu (6ES74174HL040AB0) but I will use WAGO I/Os instead of SIEMENS I/Os, I will use gateway (WAGO) instead ofCP (SIEMENS) I will use profibus but I don't know the best configuration for this system I propose configuration for this system, but I'm not quite sure from this configuration please take alook at the configuration in the attachment and inform me if this configuration true or false best regards AttachmentCPU With WAGO.zip (386 Downloads) |
1/4/2009 11:16 AM | |||
Joined: 9/27/2006 Last visit: 11/16/2024 Posts: 12294 Rating: (2691)
|
Hello ahmed; To maintain redundancy of the Profibus-DP masters on single-line slaves, Siemens recommends the use of the Y-link. For a summary description, look in the A&D Mall webpage: https://mall.automation.siemens.com/WW/guest/index.asp?nodeID=10016903&lang=en&foldersopen=-9049-9047-9035-8983-8982-8981-1-9056-&jumpto=9056
Attachedalso is a Y-link shortmanual
AttachmentY_LINK_E.pdf (362 Downloads) |
||