4/4/2019 10:58 PM | |
Joined: 9/27/2006 Last visit: 9/5/2025 Posts: 12398 Rating:
|
Hello Melhk; I believe Henri is on the right track, using the USS library you can setup the S7-200 PLC as a master to the MM4 drive; there would be no need for a Profibus-DP master (such as a S7-300) in your project, although Profibus cable and connecters are the recommended links to the drives. Check the requirements for your project and see if USS could be an acceptable solution to control a MM4 drive. Have a look at these documents: MICROMASTER (MM4), SINAMICS G120 (CU2x0x): Guidelines for reliable USS communication from PLC to an inverter https://support.industry.siemens.com/cs/ww/en/view/12462284 USS instructions in STEP 7-Micro/WIN32 with MM4 drives https://support.industry.siemens.com/cs/ww/en/view/6042107 Micro Automation: Simple networking and cascading of drives (MAS 26) https://support.industry.siemens.com/cs/ww/en/view/21690362 And study the attached pdf, it is an extract of the S7-200 System manual describing USS communications (Chapter #11). Hope this helps, Daniel Chartier AttachmentS7_200_System manual_USS protocol.pdf (730 Downloads) |
Last edited by: dchartier at: 4/5/2019 3:03:38 AM |
|
4/11/2019 8:00 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi Meihk, Profibus-plugs are for 2 cables So you can start with the CPU, then go to one slave and from that slave to the other slave. On the first and the last slave you have to put on the restistor. SIMATIC NET PROFIBUS Network Manual System Manual Slaves don´t have a program, they just have inputs and/or outputs, which are acting as an interface to controll the slave. hope this helps, regards, |
Last edited by: mopS04 at: 4/11/2019 8:11:03 AMFCK WAR! |
|
4/22/2019 3:43 AM | |
Joined: 3/21/2019 Last visit: 4/22/2022 Posts: 23 Rating:
|
Hi dchartier, It was my fault not reading that step. So now I think it's ok for me to work out the connection However I'm trying to config the connection using TIA portal but I cannot find the similar tab to this. So is this possible to do with TIA portal or I have to use Step 7? Thank you |
Last edited by: Meihk at: 4/22/2019 3:55:01 AM |
|
4/23/2019 3:41 AM | |
Joined: 3/21/2019 Last visit: 4/22/2022 Posts: 23 Rating:
|
Hi dchartier, I'm not sure if you're asking for this but here: in the EM277 properties I only see a tab to change V-memory offset and another tab to set the Start address (the 1st pic, I changed it to 10). And then I go to S7-300 properties, there's a tab to review that address, but the size was 0 and I cannot change it (the 2nd pic). Also, if I execute the project using Step7, I see in the example, the Master has some intergrated DI and DO, and they set the Input address I10..12 and Output address O10..11 (the 3rd pic). Then in the EM277, they set up the Input 10..11 and Output 10..11. But when I do the same, it said that the addresses (10..11) have been used and automatically change it to 12..13 (the 4th pic). So I wonder if DI/DO addresses set up in Master related to my project? And if I use another module as master which don't have any DI/DO inside it, do I need to have an external module for it?
[snip] Attachmentphoto-20190424T053029Z-001.zip (402 Downloads) |
Last edited by: Jen_Moderator at: 4/24/2019 7:31:50 AMRemoved link and added file as an attachment. |
|
5/14/2019 12:09 PM | |
Joined: 9/27/2006 Last visit: 9/5/2025 Posts: 12398 Rating:
|
Hello Meihk; You canot start a MM4 drive by simple sending it a Control Word value of w#16#047E. The drive must see a rising edge on the LSB of the Control Word in order to start. So you need to write to the Control Word first w#16#047E on one network, then w#16#047F in the next. MICROMASTER 4 (MM4): Setting up an MM4 with a Profibus module https://support.industry.siemens.com/cs/us/en/view/8894363 Note that you also need to have sent a Speed Reference word to the drive, if not the drive will run at 0 speed: it will not turn, just vibrate a bit. The Speed reference is related to the Max. frequency parameter of the drive, w#16#400 means 100% of that value, w#16#200 means 50%, w#16#1000 means 25%... In this link there are 4 sample programs showing how to control a Siemens drive ( S7-300, Step 7 v5.x). Open the first one ( Load/Transfer instructions) if you want to study the most basic controls if the MM4. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 05/14/2019 21:39:39 |
|