Have a look at the specifications that @AutoGen_1835473 gave in the start of the topic. Make sure you comply.. especially the firmware version. (PLC S7-1200 G2 Midbus RTU communication problem) Record the fault state of the ..Load instruction. Note that the error state is held only for one scan. So you need to capture (store) the error state value in a tag. Analyse the error identity for a remedy. Show a screen capture of your situation thereafter. Place multiple images in a ZIP. Use the classic forum interface to attach that ZIP to your response. |
Last edited by: qwazee at: 09/18/2025 11:37:12add link to original topic Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
9/22/2025 8:18 AM | |
Joined: 7/30/2024 Last visit: 9/23/2025 Posts: 978 Rating:
|
New question published by thainguyen99.haui is split to a separate thread with the subject PLC S7-1200 G2 Modbus: modbus_comm_Load block Done pin not true. Best regards |