Dear Experts, I have the below configuration & Problems, anyone have a solution on below issue, error files are attached. S7 400 FH System CPU: 6ES7 412-5HK06-0AB0 – S7 412-5H IM: 6ES7 155-6AU01-0CN0 – IM155 6 PN/2 HF FDI: 6ES7136-6BA00-0CA0 – F-DI 8x24 Vdc HF FDO: 6ES7136-6DC00-0CA0 – F -DO 8x24 Vdc HF FAI: 6ES7136-6AA00-0CA1 - F-AI- 4Xi 4-20mA HF We used theSimatic Manager V5.6 SP2 HF5Software to configure the project. In Hardware Catalogue (Refer 01 HW catalogue image) havingtwo IM155-6 GSD’sAvailable. Category 2.
Category 1.
AttachmentError.zip (460 Downloads) |
10/3/2021 5:21 PM | |
Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12296 Rating: (2691)
|
Hello Er Mack; You have configured your IM 155-6 PN through its gsd file? If you look at the M 155-6 PN/2 HF manual, you will find ths compatbility table that states you cannot setyup this IM with a S7-400H using a gsd file... https://support.industry.siemens.com/cs/ww/en/view/73184046/119328792331 Depending on the version of step 7 you are using, the IM 155-6 should be available in the Profibus catalog from version 5.6 ,for version 5.5 SP3 you would have to downoad and instal HSP 233 (or request it from Product Support through a Support Request). Hope this helps, |