Joined: 1/16/2018 Last visit: 8/8/2024 Posts: 3 Rating: (0) |
The same thing happened to me with an S7315, the problem was that I wanted to download a very large DB, even though the portal did not give compilation errors, when downloading a DB with an amount of data greater than 16383 bytes. Tia portal returned that error to me.
------------------------------------------------------------------------------------------ |
Last edited by: MaP_17 at: 11/25/2022 17:12:41Last edited by: Jen_Moderator at: 11/28/2022 04:47:17New subject after splitting. Quote inserted. |
|
11/26/2022 8:55 PM | |
Joined: 1/21/2013 Last visit: 10/3/2024 Posts: 3156 Rating: (490) |
Hi MaP_17, you should take a look at the technical data of your PLC. E.g. a CPU 315-2DP (6ES7315-2AG10-0AB0) has a limit of 16 kbyte for data blocks. Kind regards |
This contribution was helpful to1 thankful Users |