1/20/2022 7:11 PM | |
Joined: 2/17/2020 Last visit: 9/20/2024 Posts: 1062 Rating: (192) |
hi AndryG, Pls make sure that the requirements for WebNavigator are fulfilled according to the manual, at least these points: - Installing the Internet Information Server (IIS) - Internet Explorer settings (Web Navigator client) - Administering the users for WebNavigator Client Has a start image been configured for the user? Finally, have you been able to try using the WinCCViewerRT application instead of IE? |
A rating will be well appreciated. |
|
1/30/2023 3:32 PM | |
Joined: 11/7/2022 Last visit: 9/16/2024 Posts: 7 Rating: (0) |
We've been able to fix of our issues with the registry fix in this article https://support.industry.siemens.com/cs/ww/en/view/109814515 |
Last edited by: Jen_Moderator at: 02/10/2023 10:47:54Link optimized. |
|
This contribution was helpful to3 thankful Users |
1/31/2023 9:49 AM | |
Joined: 1/19/2017 Last visit: 9/17/2024 Posts: 12 Rating: (0) |
Many thanks That solved my problem. Best regards |